what size wire or what options
See BS7671......................what size wire or what options
Voltage Drop
Minimum Conductor Size
2.80%
350 kcmil
2 conductors per phase utilizing a 350 kcmil Copper conductor installed Direct Buried will limit the voltage drop to 2.80% or less when supplying 0200 amps for 750.0 feet on a 0240 volt 3 phase system.
Engineering information only
310
Amps Rated ampacity of selected conductor
0.038
Ohms Resistance (Ohms per 1000 feet)
0.04
Ohms Reactance (Ohms per 1000 feet)
0.9
Power Factor
7.199999999999999
Maximum allowable voltage drop at 3%
6.708
Actual voltage drop loss at 2.80% for the circuit
Step up/step down may or may not cost less than larger conductors alone.So to answer your question, do a voltage drop calc based on the connected load. If its really 200 amps, that will be an expensive for the correct size feeder. If it really is 200 A then consider a step up to 480, and then step back down to 120/240.