I had a situation last week (with the record breaking heat) where a roof-top AC unit was blowing one of its 30 amp time delay fuses in the disconnect and shutting down the unit. My first reaction was to replace the fuse and clip an amp probe on to see what was happening. The unit had a 3-phase, 208V input. According to the nameplate info the max. draw on any leg should have been 19.6 amps. I had an analog meter with me showing two of the legs drawing approx 24 amps and one drawing approx 18 amps. That didn't seem too far out of line so I closed up the disconnect, waited around for a half hour or so to make sure it kept running OK and left. However, a half hour after I left it shut down again.
I went back the following day with the AC guy (who claimed it was an electrical problem and not an AC problem) and re-opened the disconnect, replaced the fuse and powered up the unit. I clipped my analog amp probe on the problem leg and he clipped on his digital amp probe. In a matter of five minutes or so I saw my analog meter reading go from 24 amps to 40 amps for about 5 seconds and then drop down but, his digital amp probe display didn't move. I also tested for a change in voltage but all phases to ground remained the same at approx 120 VAC and phase to phase approx 208 VAC. We then proceeded to check every connection point from the disconnect, to the sub-panel to the feeder distribution panel and all connections were tight. I would not have even gone down to the distribution panel except for the fact that the AC guy claimed that just this season three out of the eight units on the roof were experiencing the same problems.
Now, it is my thinking that a fuse blows because something on the load side is causing an increase in amperage. Could a loose connection on the distribution side cause the same scenario ? Any thoughts or opinions would be appreciated. Also, is it common for digital amp probes to not react as quickly as analog ones do ?
Thanks in advance,
Phil
Gold Star Electric,
New Jersey
I went back the following day with the AC guy (who claimed it was an electrical problem and not an AC problem) and re-opened the disconnect, replaced the fuse and powered up the unit. I clipped my analog amp probe on the problem leg and he clipped on his digital amp probe. In a matter of five minutes or so I saw my analog meter reading go from 24 amps to 40 amps for about 5 seconds and then drop down but, his digital amp probe display didn't move. I also tested for a change in voltage but all phases to ground remained the same at approx 120 VAC and phase to phase approx 208 VAC. We then proceeded to check every connection point from the disconnect, to the sub-panel to the feeder distribution panel and all connections were tight. I would not have even gone down to the distribution panel except for the fact that the AC guy claimed that just this season three out of the eight units on the roof were experiencing the same problems.
Now, it is my thinking that a fuse blows because something on the load side is causing an increase in amperage. Could a loose connection on the distribution side cause the same scenario ? Any thoughts or opinions would be appreciated. Also, is it common for digital amp probes to not react as quickly as analog ones do ?
Thanks in advance,