anbm

Senior Member
Location
TX
Occupation
Designer
Does anyone have a wiring control diagram to show 3-phase (480V) motor to interlock with single phase (120V) motor. I.e. if the 3-phase motor runs, the single phase motor will run.
Assuming both motors have their own starter.
 

retirede

Senior Member
Location
Illinois
Use a normally open contact on the 480 volt starter to energize the coil on the 120 volt starter

Sent from my LML211BL using Tapatalk

Or the other way around, depending on the application. For example, if the larger 3 phase motor was driving a compressor and the small motor was a cooling fan for the compressor, we would always use the aux contact from the fan starter to energize the compressor starter. That way, if for any reason the fan starter doesn’t pull in, the compressor doesn’t run.
 