3 phase asymmetrical load calc

Status
Not open for further replies.

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
I think I'm having a senior moment. This is a 3 phase, two element water heater (booster). What is the actual current on leg B?

Please forgive my drawing skills

three-phase-three-wire-y-connection.jpg
 
It's a problem in vector algebra. The sum of the current vectors going into the BØ node between the two resistors has to add up to zero.

IA+IB+IC =0 IB=-IA-IC

The resistors are connected line-to-line so the voltage won't be at the same phase angles as the line-to-neutral voltages given. The current will be in-phase with the line-to-line voltage across the respective resistor. So calculate the voltage vectors first:

VAB = VA-VB = 120/0° - 120/120°
VBC = VB-VC = 120/120° - 120/240°

Then use Ohm's law to calculate the currents in A & C, which you can use to solve the first equation.

Do you know how to add and subtract the vectors?
 
The short answer is that when you add two identical currents I that are 60 degrees out of phase, the sum is not 2 * I , but sqrt(3) * I. So the answer is 20A * sqrt(3) = 34.6A.

That's what the previous answer boils down to in this special case, which arises often enough that I find it a useful shortcut to remember.

Cheers, Wayne
 
The short answer is that when you add two identical currents I that are 60 degrees out of phase, the sum is not 2 * I , but sqrt(3) * I. So the answer is 20A * sqrt(3) = 34.6A.
Thanks Wayne. 1.73 was what came into my head at first but then for some reason I had doubt.. This is the 3rd time I've had to reengineer this whole heater relocation because I was getting bad info from the field. First they told me there was 480 3 phase available, then that changed to single phase 208, and when I went and looked for myself it was 208 three phase. It was originally powered by 480 three phase in it's old location.
Do you know how to add and subtract the vectors?
Thanks Joe. I need to refresh myself with the math. I did know it at one time, but when I tried to remember I realized I hadn't done it in quite a few years
 
@Joethemechanic ,
If that resistive load was supplied by 480V, 3-phase before, the load amps on the B leg would be 34.6A. But since the new source was verified by you to be 208V, 3--phase, the current on leg B will be 15.01A (Ohmic value of resistors = 480/20 = 24 ohms, Amps on 208V = 208/24 = 8.67A and leg B amps = 8.67 X 1.732 = 15.01A)
 
@Joethemechanic ,
If that resistive load was supplied by 480V, 3-phase before, the load amps on the B leg would be 34.6A. But since the new source was verified by you to be 208V, 3--phase, the current on leg B will be 15.01A (Ohmic value of resistors = 480/20 = 24 ohms, Amps on 208V = 208/24 = 8.67A and leg B amps = 8.67 X 1.732 = 15.01A)
Had to order the correct elements this morning. The 208v ones were where the 20 amp number came from. Had to order a different control transformer and a bunch of stuff. Every time I had it all figured out, they changed the voltage or the phases on me
 
Sorry, my guess was you had a homework problem and not a real-world application. I was trying not to give you the answer.
No problem, Nahhh, not homework, I'm almost 62 and was having a senior moment. Too many changes in what I was designing in a short period of time. I appreciate your help
 
Actually it is not a sum but a difference.
 

Attachments

  • 3 phase asymmetrical load calc.jpg
    3 phase asymmetrical load calc.jpg
    118.3 KB · Views: 10
What's the difference between a sum and a difference? Do two differences make a sum?
Sum / difference impacts the direction of vectors. A difference is essentially a sum with one of the vectors in the opposite direction (rotated 180 degrees).

As noted in post#3, you're looking for the sum of two currents 60 degrees out of phase. Post #2 gives the context on how to get to 60 degrees. Solving the vector addition graphically using 30/60/90 triangles is probably the easiest way to get the resultant vector magnitude of 20*sqrt(3).
 
Sum / difference impacts the direction of vectors. A difference is essentially a sum with one of the vectors in the opposite direction (rotated 180 degrees).

As noted in post#3, you're looking for the sum of two currents 60 degrees out of phase. Post #2 gives the context on how to get to 60 degrees. Solving the vector addition graphically using 30/60/90 triangles is probably the easiest way to get the resultant vector magnitude of 20*sqrt(3).
A vector is called a vector because it has in itself a direction aside from its magnitude. IMO, the correct term used is "summation of vectors".
 
Do two differences make a sum?
Sort of. Though there will still be a difference kicking around at the end of the day.

The difference between B and C is subtracted from A, to make the difference between A and (B - C):
A - (B - C)

When you distribute the negative sign, this simplifies to:
A - B + C

Which we can rearrange to make it more intuitive to understand:
A + C - B

It started as two nested differences, and now it simplifies to a sum and a difference.
 