Thanks Wayne. 1.73 was what came into my head at first but then for some reason I had doubt.. This is the 3rd time I've had to reengineer this whole heater relocation because I was getting bad info from the field. First they told me there was 480 3 phase available, then that changed to single phase 208, and when I went and looked for myself it was 208 three phase. It was originally powered by 480 three phase in it's old location.The short answer is that when you add two identical currents I that are 60 degrees out of phase, the sum is not 2 * I , but sqrt(3) * I. So the answer is 20A * sqrt(3) = 34.6A.
Thanks Joe. I need to refresh myself with the math. I did know it at one time, but when I tried to remember I realized I hadn't done it in quite a few yearsDo you know how to add and subtract the vectors?
Had to order the correct elements this morning. The 208v ones were where the 20 amp number came from. Had to order a different control transformer and a bunch of stuff. Every time I had it all figured out, they changed the voltage or the phases on me@Joethemechanic ,
If that resistive load was supplied by 480V, 3-phase before, the load amps on the B leg would be 34.6A. But since the new source was verified by you to be 208V, 3--phase, the current on leg B will be 15.01A (Ohmic value of resistors = 480/20 = 24 ohms, Amps on 208V = 208/24 = 8.67A and leg B amps = 8.67 X 1.732 = 15.01A)
Sorry, my guess was you had a homework problem and not a real-world application. I was trying not to give you the answer....Thanks Joe. I need to refresh myself with the math. I did know it at one time, but when I tried to remember I realized I hadn't done it in quite a few years
No problem, Nahhh, not homework, I'm almost 62 and was having a senior moment. Too many changes in what I was designing in a short period of time. I appreciate your helpSorry, my guess was you had a homework problem and not a real-world application. I was trying not to give you the answer.
What's the difference between a sum and a difference? Do two differences make a sum?Actually it is not a sum but a difference.
Sum / difference impacts the direction of vectors. A difference is essentially a sum with one of the vectors in the opposite direction (rotated 180 degrees).What's the difference between a sum and a difference? Do two differences make a sum?
A vector is called a vector because it has in itself a direction aside from its magnitude. IMO, the correct term used is "summation of vectors".Sum / difference impacts the direction of vectors. A difference is essentially a sum with one of the vectors in the opposite direction (rotated 180 degrees).
As noted in post#3, you're looking for the sum of two currents 60 degrees out of phase. Post #2 gives the context on how to get to 60 degrees. Solving the vector addition graphically using 30/60/90 triangles is probably the easiest way to get the resultant vector magnitude of 20*sqrt(3).
Sort of. Though there will still be a difference kicking around at the end of the day.Do two differences make a sum?