Grouch
- New York, NY
Hi all,
I have a question regarding the picture I attached... it's an example from Cooper Bussmann's SPD Handbook (2005 edition). the left diagram shows how the #10 EGC is not properly rated for the 50,000 amps of short circuit current. #10 wire is only rated for 4,300 amps at a 1 cycle opening time of a OCPD. however, the diagram on the right shows the #10 wire is now properly protected by using current limiting fuses that limit the current down to 3,300 amps.
My question is... it seems like the 50,000 amps of current they are using as an example seems to be the 3 phase current you get assuming all phase legs are bolted together. shouldn't this number be the ground fault current instead, since we are determining the amount of fault current going along the EGC?
Thanks!
Thanks!