I came across a 3 phase 208 breaker feeding 6) 208V single phase loads. Each load is tapped to 2 phases of the 3 phase breaker. The 6 loads are generally distributed evenly across the phases. There is a 8/3 MC pulled to a Jbox. From there, 12-2 MC is distributed to each HVAC units
1) Can a 3 phase breaker be tapped like this (rather than using multiple double pole breakers and another wire out to loads) Theoretically the branches will not see the entire load of the circuit, only their individual draws. Isn’t there a tap rule for this situation? I haven’t found anything yet
2) Can the 12/2 taps be in a circuit fused at 40 amps, without additional step down fusing to 20 amp?
3) Since there is a fractional HP fan motor, do I also need to simultaneously disconnect both phases on overload, or will the manufacturers safeties handle that?
Thanks