When a panel is fed through a 3 phase breaker and one of the phases is higher than the rated current does the breaker trip.
All of your questions appear to be homework or study questions, is this the case?When a panel is fed through a 3 phase breaker and one of the phases is higher than the rated current does the breaker trip.
Common breakers are "inverse time" rather than "instantaneous trip" type. They will trip on overcurrent, but how long and if it in fact does varies with the amount of time and level of overcurrent. Google "breaker time curves".When a panel is fed through a 3 phase breaker and one of the phases is higher than the rated current does the breaker trip.
Wow, this is the first time you have replied to anyone. I was beginning to think you only wanted answers.No, these are not homework questions.
Not to mention that it is impossible to make all the trip points precisely equal.In fact, you could say that it is ALWAYS only one that causes the trip, because it is virtually impossible for more than one pole to carry the absolute exact same amount of current.