220/221 said:There ARE residential applications where the panel is 3 phase and the high leg only goes in and out of the 3rd pole of the special breaker.
See 240.85 for an explanation. The 120/240 means that where the nominal voltage of any conductor to ground does not exceed the lower of the two values of the circuit breaker's voltage rating is where it is permitted to be used.
220/221 said:... But....how could/why would a 3 pole breaker be rated 120? ...
coulter said:Wouldn't a 240/120 slash rating be okay in a 208/120, 3 ph panel?
carl
kencoel said:OK, somewhat confused with multiple answers. But...I believe then that a standard 3P breaker can be used when there is a delta phase connected?
220/221 said:My bad...I assumed something.
But....how could/why would a 3 pole breaker be rated 120???
Bear with me. I am slow sometimes
Oh...yeah that![]()