Picture a single-phase service. Now substitute the two line conductors for the two ungrounded corners and the neutral for the grounded corner. Now where would you get the EGC?Looked at a job today to run wiring to new water heater. the panel was 200 amp 3 phase corner grounded delta #3/0 wire from meter base to 3 pole 200 amp breaker in panel no EGC in panel how do i get a EGC?
Is this the service panel or a sub panel?I understand how a corner grounded works . what i want to know is where to connect the EGC to .the wires to the panel are in 2" rmc with no grounded bushing and go to a 3 phase breaker . where do i tap the EGC to ?
In that case the installation may never have been complete according to code. The grounded incoming conductor and a ground electrode conductor from somewhere need to be connected and bonded to the enclosure (unless that bonding was done upstream in the meter enclosure?)It is a 200 amp service.
I agree with with all replies. BUT WHERE DO I TAP EGC TO?
One way to do it is to attach a lug to the metallic panel enclosure or since this is a service go right to the "neutral" bar.
I meant bonding jumper .
I believe he's saying there is no main bonding jumper.Not sure you are on same page as other people that have replied.
A properly installed service will have the grounded service conductor bonded to the service equipment enclosure already. ...
Amounts to, he will have to install one to make his installation compliant, regardless of it not being compliant previously. He'll have to "tap" the grounded supply conductor and connect the other end to a grounding terminal bus (or use any other approved means).