How accurate is the current measurement in the third leg when you amp two of the 3 legs together?
If it is a balanced 3 phase load then I1 + I2 + I3 = 0
If you know two of the three phases, then you know the third I1 + I2 = -I3
How accurate is the current measurement in the third leg when you amp two of the 3 legs together?
If it is a balanced 3 phase load then I1 + I2 + I3 = 0
If you know two of the three phases, then you know the third I1 + I2 = -I3
If it is a balanced 3 phase load then I1 + I2 + I3 = 0
If you know two of the three phases, then you know the third I1 + I2 = -I3
Even if it is an unbalanced 3 phase load (no neutral) the same equations would apply.
Is it possible for there to be a delta system (no neutral) that is unbalanced?
Without a neutral, what would carry the unbalanced current?
It can certainly be unbalanced in that the three line currents are not equal.
Consider, for example, a 208Y/120 that has a 10A load from A to C. The current in B is zero. That is unbalanced but has no neutral current.
Put two ten amp single phase loads on any three phase system connected A to B and B to C. A draws 10 amps, C draws 10 amps, B draws 17.32 amps.