What’s up everyone? I have a 3 phase 208v motor, 37amps, coming off VFD, diagram on pecker head , showing a delta and Y connection. I want to make sure since it is just a 3 phase with ground coming in I’m hooking up with the delta diagram correct. My understanding the wye would only be used if I had a neutral coming in. Am I understanding that correctly? Thanks
 

Brownetown

Member
Location
Va
Occupation
Electrican
I can tomorrow,the motor does only state 208v so there is no way it could have another configuration for 480v, do you think there could be a start or triangle next to it that I might of missed?
 

Brownetown

Member
Location
Va
Occupation
Electrican
I wanna say 6 v1-v2
U1-u-2
W1-w2

I believe those were the connections already established. I also wanna say the motor arrived configured as delta.
 

Jaybone812

Member
Location
Massachusetts
Occupation
Electrician
What’s up everyone? I have a 3 phase 208v motor, 37amps, coming off VFD, diagram on pecker head , showing a delta and Y connection. I want to make sure since it is just a 3 phase with ground coming in I’m hooking up with the delta diagram correct. My understanding the wye would only be used if I had a neutral coming in. Am I understanding that correctly? Thanks

Delta motor configuration would be 3 ungrounded phase conductors and a egc, the delta won’t need a neutral


Sent from my iPhone using Tapatalk
 

Jaybone812

Member
Location
Massachusetts
Occupation
Electrician
A 3 phase motor would never have a connection to the center point of the wye configuration, either.
Unless there’s some weird thing I haven’t seen before.

You’re 100% correct . No connection to center point of wye, so no neutral . He’s confusing delta /wye motors with delta /wye systems or transformers .


Sent from my iPhone using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I can tomorrow,the motor does only state 208v so there is no way it could have another configuration for 480v, do you think there could be a start or triangle next to it that I might of missed?
Wye or delta is how the windings in the motor are connected to each other. With a six lead motor you would put the windings in delta for low voltage hook up and wye for high voltage. Either way you never use a neutral for a three phase motor.
d8014046034569bcf75d998647e2a781--pumps-motor.jpg

In your case there is no high voltage option.
 

James.taylor

Member
Location
San Antonio Texas
Occupation
Electrical
Wye or delta is how the windings in the motor are connected to each other. With a six lead motor you would put the windings in delta for low voltage hook up and wye for high voltage. Either way you never use a neutral for a three phase motor.
d8014046034569bcf75d998647e2a781--pumps-motor.jpg

In your case there is no high voltage option.
100% from my 25 years of experience! I have yet to see a 3 phase motor need a nuetral and if so it was for the controls which were seperate circuits from the motor circuit.
 

Jaybone812

Member
Location
Massachusetts
Occupation
Electrician
Wye or delta is how the windings in the motor are connected to each other. With a six lead motor you would put the windings in delta for low voltage hook up and wye for high voltage. Either way you never use a neutral for a three phase motor.
d8014046034569bcf75d998647e2a781--pumps-motor.jpg

In your case there is no high voltage option.

Exactly . Low volt delta and high volt wye configurations end up with a identical hp where as hooking this 208 motor up to wye will lead to a lesser hp than the delta configuration