I had a building I was in (120/208 3 phase) start acting weird. Some of the lights were working, the battery backup troffers were flashing, whole sections of the building not working.
After testing I found that A and C phase had about 65 volts to ground and B phase had 120. The power company said that we had lost a leg, but the symptoms looked more like a dropped neutral.
Can any of you explain this? It seems that if we lost a single leg that we wouldn't have any voltage on that leg to ground.