Abhi
I m an Engineer
- Location
- Jharkhand, India
- Occupation
- Electrical & Instrumentation Engineer
I have 3 phase motor of rating 3 kw, rpm=960, flc=6.5amp, volt=415v, resistance= 3.5ohm
I was performing polarity test of winding, so i applied 230v ac supply to one of its winding. But the motor started and running with low rpm and afterwards smoke came out of its winding. I switched off the power supply immediately.
Connections for the polarity test was absolutely correct. So nothing wrong there.
Then I connected motor in delta connection and current was 53amp and again I changed it to star connection and now current was 5.5amp.
There is nothing wrong in measured values provided by me. So there should be no doubt about it. I shared here what I experienced.
So my question is why this happened and does motor runs during polarity test.
I was performing polarity test of winding, so i applied 230v ac supply to one of its winding. But the motor started and running with low rpm and afterwards smoke came out of its winding. I switched off the power supply immediately.
Connections for the polarity test was absolutely correct. So nothing wrong there.
Then I connected motor in delta connection and current was 53amp and again I changed it to star connection and now current was 5.5amp.
There is nothing wrong in measured values provided by me. So there should be no doubt about it. I shared here what I experienced.
So my question is why this happened and does motor runs during polarity test.