D designer82 Senior Member Location Boston Dec 20, 2022 #1 If I have a 60kW-3 phase heater load, how many kilowatts will be going through each one of the 3 phases?
If I have a 60kW-3 phase heater load, how many kilowatts will be going through each one of the 3 phases?
W wwhitney Senior Member Location Berkeley, CA Occupation Retired Dec 20, 2022 #2 The word "phase" is overloaded and can have different meanings. But as long as you stick with one particular meaning, then by symmetry it will be 60/3 = 20 kW. Cheers, Wayne
The word "phase" is overloaded and can have different meanings. But as long as you stick with one particular meaning, then by symmetry it will be 60/3 = 20 kW. Cheers, Wayne