3 phase LED branch circuits- finding amps

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Just wanna be sure on this…I have two, three phase, three pole 480V branch CBs from a panelboard feeding two strings of 35 floodlight LEDs each. The vendor data shows average system watts of 459 per fixture. Initially I assumed I should calculate the amps as if it were a typical three phase circuit meaning W divided by V x PF x 1.73. But the fixtures themselves are only single phase. So should the branch circuit also be calculated at single phase 480V, instead of three phase?


Sent from my iPhone using Tapatalk
 
Depends how the strings are wired. Are they two wire or three wire? If you round up to 1 amp per light and you balance 35 lights over 3 phases you'd something like 24,23 and 23 Amps approximately on the three phases. If its two wire you'd have 35,35, 0 per string.
So with two wire your highest loaded phase could have 70A and three wire 48A
 
Last edited:
Depends how the strings are wired. Are they two wire or three wire? If you round up to 1 amp per light and you balance 35 lights over 3 phases you'd somthing like 24,24 and 22 Amps approximately on the three phases. If its two wire you'd have 35,35, 0 per string.
So with two wire your highest loaded phase could have 70A and three wire 48A

They are wired a with three wires plus ground


Sent from my iPhone using Tapatalk
 
480V Line to Line connected, so a delta connected load so to speak.
Each light will put about 1 Amp on two legs.
 
Just wanna be sure on this…I have two, three phase, three pole 480V branch CBs from a panelboard feeding two strings of 35 floodlight LEDs each. The vendor data shows average system watts of 459 per fixture. Initially I assumed I should calculate the amps as if it were a typical three phase circuit meaning W divided by V x PF x 1.73. But the fixtures themselves are only single phase. So should the branch circuit also be calculated at single phase 480V, instead of three phase?


Sent from my iPhone using Tapatalk
Please clarify how are the loads connected. Are the LEDs connected in wye (277V) or in delta (480V)? 35/11 =11.67, take 11 LEDs on two of the phases and 13 LEDs on the third phase. Assuming a unity PF the line currents are:
  • On the first arrangement (wye), the line currents will be Ia = Ib = 18.22A, Ic = 21.53A, In = 3.31A.
  • In the second arrangement (delta), the currents will be Ia = 19.9 A, Ib = 18.22A, and Ic = 19.9A.
 
Please clarify how are the loads connected. Are the LEDs connected in wye (277V) or in delta (480V)? 35/11 =11.67, take 11 LEDs on two of the phases and 13 LEDs on the third phase. Assuming a unity PF the line currents are:
  • On the first arrangement (wye), the line currents will be Ia = Ib = 18.22A, Ic = 21.53A, In = 3.31A.
  • In the second arrangement (delta), the currents will be Ia = 19.9 A, Ib = 18.22A, and Ic = 19.9A.

Line to line 480V across all three phases=A/B, A/C and B/C…no neutral to 277V


Sent from my iPhone using Tapatalk
 
But the branch calculation is still using sq root of 3. Correct?
To size the branch circuit I use the highest loaded leg.
And then add the continuous factor.
For the service / feeder load calc I would just keep it in VA
and add the continuous factor to the VA.
 
First you need to confirm that the strings are wired as a three phase load. I know you say you have 3 wires, but confirm that the manufacturer of the string used all 3 wires and tried to balance things.

If you have N matched single phase loads distributed across 3 phases in as balanced a fashion as possible, my approach is to first find the nearest multiple of 3 greater than or equal to N.

Take this multiple of 3, times the watts per individual load, and then use the 3 phase current equation.

In your case I would use 36 * 459 / V / pf/ 1.732

Jon
 
First you need to confirm that the strings are wired as a three phase load. I know you say you have 3 wires, but confirm that the manufacturer of the string used all 3 wires and tried to balance things.

If you have N matched single phase loads distributed across 3 phases in as balanced a fashion as possible, my approach is to first find the nearest multiple of 3 greater than or equal to N.

Take this multiple of 3, times the watts per individual load, and then use the 3 phase current equation.

In your case I would use 36 * 459 / V / pf/ 1.732

Jon

I agree with your calculation-
thanks
Isaiah


Sent from my iPhone using Tapatalk
 