3 phase line filters melting out.
lquadros
3 phase line filters have failed/ melted due to supposedly capacitor failures within these filters. What would be the reasons that it would do so?
Any answers would be greatly appreciated.
How old are the capacitors? I had a motor starter that melted that had starting capacitors. Capacitors fail just like any other electric components. Depending on how old the capacitors are the electrolytic could of deteriorated.
What kind of load do you have on the filter outputs? High frequency content from nonlinear loads or other sources may cause large currents to flow through the capacitors because of their decreasing impedance as the frequency goes up. High currents will heat capacitors because of their series resistance (which is spec'ed as their ESR or equivalent series resistance).
Or is the line filter on the output of a VFD or other source with higher frequency switching content? The same effect can occur due to high currents in the capacitors. The filter should have series inductors, at least on the side where the high frequency content originates, in order to limit the current going through the capacitors.
What are these "filters" anyway? Are they one of these snake-oil magic box products that was supposedly going to save them energy? Those things are all total junk, not worth the time to install them.
I have seen harmonics from non-linear loads cause that.
The 3phase line filter is connected to 6 axis servo motors. A robot. The load is non-linear.
At the moment, the focus is on Harmonics. I need to understand more about this. The solution arranged is to install the line filter on the secondary side of the transformer instead of Primary. Any ideas?