3 phase load calculation
KHall
I have a 3 phase panel with 7 different 208V/1 phase loads. I calculated the load for each 2 pole circuit by multiplying the load amps by 208. The VA totals for each phase are as follows ...
A = 18,242 VA
B = 18,242 VA
C = 16,224 VA
How do I convert this into a total connected load figure for this panel and would that (along with 25% of my largest motor) be the basis for sizing my feeder and main breaker?
The system is 120/208, 3 phase, 4 wire.
A = 18,242 VA
B = 18,242 VA
C = 16,224 VA
[Minimum] sizing of main breakers and feeders are done through Article 220 calculations under Patrs III, IV, and/or V. There are quite a few factors which impact the minimum sizing, including continuous and non-continuous loads. The calculations are the only NEC-compliant method.
In determining size for imbalance, your loads, as distributed on the phases, will have to be converted to line current and weighed against the minimum size as calculated to determine if larger sizing is required.
more help
more help
I am reasonably familiar with the NEC rules on sizing feeders and equipment. It's the 3 phase calculations that I don't work with very much. I need help to understand how to take the A,B, & C volt-amp totals and convert that to a single amperage figure for calculating my feeder and equipment sizes. The loads are all HVAC equipment that will be continuous loads.
Thanks!
A = 18,242 VA
B = 18,242 VA
C = 16,224 VA
What is the individual VA ratings of the 7 individual circuits. If you calculated this wrong you could easily have high totals. I see you as reporting a total of about 52.7 KVA. I could also see you actually having a total load of about 26 KVA depending on how you came up with the numbers you posted.
Find out what the total load is @ 208 volt single phase then work on dividing it up across the three phases. If all seven loads are equal you can easily come up with a balanced per phase load for six of the circuits and then add the unbalanced portion of the seventh to two of the phases.
First thing is to know the VA ratings of the individual circuits.
A = 18,242 VA
B = 18,242 VA
C = 16,224 VA
Simply, the highest load must be accommodated, so you need to use the largest number to figure the load current. In this case, you have two lines with 18.242kva loading.
I would also like to see this calculation. I see it as simply 18242va/ 208 but I am not sure that is correct. Then what do you do with 3 different currents all single phase 208V
A = 18,242 VA
B = 18,242 VA
C = 16,224 VA
A 18.2kva/.120 = 152 amps
B 18.2kva/.120 = 152 amps
C 16.2 kva/.120 = 135 amps
Combining all the load 18.2 + 18.2 + 16.2 = 52.6
52.6 kva/0.208 x 1.73 = 146 amps
If you assume the load was balanced 3 x 18.2 = 54.6
amps = 54.6 /.208 x 1.73 = 152 amps
A = 18,242 VA
B = 18,242 VA
C = 16,224 VA
Your VA load does equal 52,708VA if this were the total VA result of an Art 220 calc you?d have an 87A calculated load but to arrive at this there is a method to follow something like below:
10,000 (first 10kva at 100%)
21,354 (remainder at 50%)
31,354 (total non-continuous load - not likely all non-continuous)
0 total (continuous load - not likely zero)
0 (largest motor at 25% - probably have this too)
31,354 (total VA)
87 (total Amperes VA/208/1.732)
I suggest using an example in the annex D (D3) to calculate your load and be compliant.
individual circuit ratings
I hope I got this part of it right. The seven loads are not equal. I think they are as balanced across all three phases as much as possible. I calculated the individual circuit rating by taking the load current and multiplying by 208. For example, one heat pump has a MCA of 30A. 208x30=6240VA. I applied that amount (6240) to each of the two phases that circit is connected to. Correct?
That is where I was going with my question. If you balance the load each phase carries 1.73 times the single phase current.
You also only need to calculate with actual load not MCA marked on the unit. The MCA is for sizing the conductors for the branch circuit and is likely 125% of the compressor RLA plus all other loads in the unit or very close to that. Your feeder will need to be at least 125% of largest plus all others
Lets assume your 30 amps or 6240 VA is the actual load and you have 6 of the same units evenly balanced across all three phases. You have a total 37440 VA.
Divide by 208 gives you total single phase amps of 180 amps. Since you are balancing this across three phases you need to divide that by the square root of 3 (1.73) to get the amps per phase. Which will be about 104 amps. Now your seventh unit will be an additional 30 amps connected to each of the two phases you put it on, so you will have something like
Phase A = 134 amps
Phase B = 134 amps
Phase C = 104 amps
Remember you used the MCA to get your individual load of 30 amps. The actual full load of the unit is probably closer to 21-24 amps. If your seven units are not all the same size you will want to connect them to the phases in a way that comes closest to balancing the loads between the phases for best results as well as allowing a smaller feeder to supply them.
If you are calculate load then you would not use the mca. The mca of a heat pump/ac unit already has the 125% factored in.
Create an Excel spreadsheet just like a panel schedule with A,B,C phases on the left and right 22 +/- down each side. Total each column of A,B,C?s to view the balance of each, similar to below the put the math in from Art 220 for the totals at the bottom of the spreadsheet.
I like that. Only question is does the totals for each phase factor in the 1.73 multiplier for three phase. This would be an easy spreadsheet to make for single phase. Three phase is not impossible but the formula for total amps is a little more tricky for three phases that are not the same load per phase.
very helpful!!
very helpful!!
Phase A = 134 amps
Phase B = 134 amps
Phase C = 104 amps
This has been very instructive, but I'm not sure I've got it. If you don't mind, I am going to run thru the whole calculation ...
There are (3) 208V/1ph Heat Pumps rated 30 MCA. If I reduce them by .8, and then multiply by 208V, that will give me a 4992VA load to each of two phases.
Next, I have (3) 208V/1ph Air Handlers at 9 MCA. Same calculation results in 1498VA per phase.
Finally, one 208V/1 ph Energy Recovery Ventilator at 9.7 MCA adds 1622VA to each phase connected, which are A & B.
The HPs and AHUs can all be connected to result in a balanced load across all 3 phases. The ERV will produce a larger imbalance in the two phases (A & B) to which it is connected.
Therefore ...
Phase A = 4992+4992+1498+1498+1622 = 14,602VA
Phase B = (same as A) 14,602VA
Phase C = 4992+4992+1498+1498 = 12,980VA
Calculating the balanced portion of the load ...
12,980VA / 208 / 1.73 = 36A on each phase A, B, & C
the unbalanced portion ...
1622VA / 208 = 7.8A on phase A & B.
Compiling balanced & unbalanced amperage results in ...
A = 43.8, B = 43.8, C = 36
Final note ... add in 25% of largest motor of sizing feeder.
The final numbers seem low to me. Did I miss something??
This panel schedule calculates either 1 or 3 phase, there is an "IF" function that calculates based on the phase type entry at the top of the spreadsheet (again 1 or 3).
The panel schedule is designed to reveal an Art 220 calculated load (1 or 3 phase). The phase balances reveal using VA rather than amperes. The circuit entries are done in VA so if there is a 1ph unit with nameplate amperes 32A at 240 it would be 3840VA per phase in the entry (or 3840VA for 208 as well).
The spreadsheet calculates at the bottom based on circuit specs entered at the top.
I think you missed something. Your balanced load is three (3) 4992VA loads and three (3) 1498VA loads. That gives a balanced load of 19470VA.
19470VA balanced load at 208V, 3ph give a current of 54.04 Amps. So A, B and C would see 54.04 Amps. And adding the last unbalanced load (of 1622VA) between A and B would add 7.8 Amps to A and B.
So the total unbalanced load would be 61.84 Amps on A and B, and 54.04 Amps on C.
(As a side note, you probably can't multiply the MCA of the heat pump by 0.8 to get the load current. This would only work for a single motor load.)
?There are (3) 208V/1ph Heat Pumps rated 30 MCA. If I reduce them by .8, and then multiply by 208V, that will give me a 4992VA load to each of two phases?
Use the whole MCA in your load otherwise you need to calc it per 440 part IV. Also the 4992 would be half on each phase 2496 (4992 / 208 = 24A) but again use the 30A.
Using your numbers here?s the result: