Hello, this is my first post.
I have a question that I am hoping you all can help me with.
I am looking at a job that involves replacing (5) EVSEs. The existing (5) EVSEs are being fed from a 208 volt/3 phase panel. The panel is fed from a 3 phase, 100 amp breaker at the main source.
My question is this:
Each EVSE is 2 pole and will have a 32 amp maximum draw, and a 40 amp calculated load (125% of the maximum draw). Assuming the 100 amp panel is evenly loaded, 2 of the phases would have 120 amps and 1 phase would have 160 amp calculated load. So a 100 amp feeder is to small to handle this.
However the buildings electrical supervisor is telling me that since it is a 3 phase system each lines total Kva (208*160 = 33.2kva) can be divided over 360 volts because of 3 phase (208x1.72), bringing the highest loaded phase to a total of 92.4 amps. Making the 100 amp feed adequate.
Is this correct? I thought I could only apply that 360 voltage if the device loads were 3 phase loads, these are only using 2 legs of the 3 phase.
See link to 1 line diagram of this question.
https://drive.google.com/open?id=14rmxaSFbhigNRo2fvnd5LstEGlJA0flj
I have a question that I am hoping you all can help me with.
I am looking at a job that involves replacing (5) EVSEs. The existing (5) EVSEs are being fed from a 208 volt/3 phase panel. The panel is fed from a 3 phase, 100 amp breaker at the main source.
My question is this:
Each EVSE is 2 pole and will have a 32 amp maximum draw, and a 40 amp calculated load (125% of the maximum draw). Assuming the 100 amp panel is evenly loaded, 2 of the phases would have 120 amps and 1 phase would have 160 amp calculated load. So a 100 amp feeder is to small to handle this.
However the buildings electrical supervisor is telling me that since it is a 3 phase system each lines total Kva (208*160 = 33.2kva) can be divided over 360 volts because of 3 phase (208x1.72), bringing the highest loaded phase to a total of 92.4 amps. Making the 100 amp feed adequate.
Is this correct? I thought I could only apply that 360 voltage if the device loads were 3 phase loads, these are only using 2 legs of the 3 phase.
See link to 1 line diagram of this question.
https://drive.google.com/open?id=14rmxaSFbhigNRo2fvnd5LstEGlJA0flj