Hello,
Urgent Help!
Our warehouse has a 3 phase 277/480V 4 wires panel with a 1000A breaker.
We need to add 75-KVA step-down transformer to supply the new 200A 120/208V 3 phase 4 wire PNL and need help to confirm if the below is correct.
My electrician just completed 30-day load log and reported that,
Phase A: has 280A as a peak with an average of 112A,
Phase B: has 276A as a peak with an average of 103A, and
Phase C: has 281A as a peak with an average of 107A.
He states that 1000V*0.8 - 279V(avg. of peaks) which is 521A(equivalent to 568KVA) is available.
But my maintenance department says we can not add any more because sums of 3 phases current already exceeded 80% of 1000V and there is no room.
Who is right? And Can we add a transformer to feed 200A 120/208V PNL?
If the electrician is right, what is the maximum amount available? Can we put a larger size PNL?
Thank you for help.
Urgent Help!
Our warehouse has a 3 phase 277/480V 4 wires panel with a 1000A breaker.
We need to add 75-KVA step-down transformer to supply the new 200A 120/208V 3 phase 4 wire PNL and need help to confirm if the below is correct.
My electrician just completed 30-day load log and reported that,
Phase A: has 280A as a peak with an average of 112A,
Phase B: has 276A as a peak with an average of 103A, and
Phase C: has 281A as a peak with an average of 107A.
He states that 1000V*0.8 - 279V(avg. of peaks) which is 521A(equivalent to 568KVA) is available.
But my maintenance department says we can not add any more because sums of 3 phases current already exceeded 80% of 1000V and there is no room.
Who is right? And Can we add a transformer to feed 200A 120/208V PNL?
If the electrician is right, what is the maximum amount available? Can we put a larger size PNL?
Thank you for help.