Team-MEI
Inactive, Email Never Verified
- Location
- Vancouver, WA
I have several exterior 3-phase loadcenters with only 2P branch-circuit breakers present in the loadcenters. I cannot find an NEC section which requires a neutral in this situation. Dismissing the several merits for having the possible availability of 1P branch loads if a neutral was present; is there a code which requires a neutral where the branch loads are all 2P? I know if I do run such a neutral that it cannot be downsized per 220.22. I cannot find any special code required labeling either which would show ?no neutral present?; is there a special caution labeling requirement for this situation? I ran 2-hots and a properly sized EGC to each but no neutral. Thanks in advance for your comments.