Its been a really long day guys and I am second guessing an engineers calculations. He has phase a 17864 watts, phase b 30119 watts, and phase c 30214 watts. For his load calc he added all three together for 86460 watts and calculated out to 240 amps necassary and is now calling for a 400 amp where there is an existing 200 amp service.
I think we should take the highest leg of the unbalanced load and that would determine our service size.
Am I crazy? or just really tired? 120/208 3 phase service