3 phase motor controls

Status
Not open for further replies.

JdoubleU

Senior Member
I came a cross a 3 phase condensate pump that was controlled by a Float. The control wire did not go to a starter to energize a coil and close a 3 phase contactor. They just used one phase and ran it through the float switch. It works fine but how. Shouldn't this single phase the motor and is it legal.
 
I'd look closely. I know of no way you could just switch one phase. As Tom says, it probably switches two of the phases. Not uncommon in HVAC controls also.
 