3 phase motor questions

Status
Not open for further replies.

dodiho

Member
I am a new apprentice student...my boss has asked me the following questions....I am studying the NEC and am lost at present...#1: if I replace a three phase motor with a 115V single phase motor-will it work without modifications? #2: What is the formula for a 30 degree offset? Help! My lunch today is on the line! Dodiho
 
Re: 3 phase motor questions

#1: No. You will not be able to connect three wires (from the power supply) to two terminals (on the motor), so some type of modification will be needed. The modification should be to run a new branch circuit, starting with a single pole breaker.

#2. The question does not make sense. There is no "formula" by that name. You will have to get your boss to restate the question.

By the way: Welcome to the Forum.
 
Re: 3 phase motor questions

There's a couple of things to consider.
1) Single phase motor requires power from only one L-L connection, A-B, B-C, or B-A. That provides single phase.
2) Now for the "modification." A L-L voltage was not specified so one would have to guess what that may be. But, 3ph voltage is either 208, 240, or 480v so one of those would be your L-L single phase voltage. That leaves you with the challenge of coming up with 115v, or 120v nominal. You would have to add a 1ph transformer of a given KVA to transform the supply voltage of 208, 240, or 480v down to 120v to power the 1ph motor. Hence, the "modification."
 
Re: 3 phase motor questions

The formula for a 30 degree offset is 2 times the depth of the offset. A 15 degree offset would be 3.86 times the depth and a 45 degree offset would be 1.41 times the depth.
 
Re: 3 phase motor questions

It is also the cosecant of the angle, or if your calculator doesn't have that it is the inverse of the sine of the angle.
Don
 
Re: 3 phase motor questions

If you have 120/208 couln't you run the motor from one of the L-N voltages? Of course, this would tend to unbalance the 3-phase load.
 
Re: 3 phase motor questions

Originally posted by dodiho:
#2: What is the formula for a 30 degree offset? Help! My lunch today is on the line! Dodiho
Originally posted by charlie b:
#2. The question does not make sense. There is no "formula" by that name.
Originally posted by rattus:
Someone define "offset" as used here. I plead ignorance.
dodiho Welcome to the forum.

Don't worry, the above answers are not from electricians, they are engineers. :D

Infinity gave you some exact figures but I just use the following.

15 degrees 4 times the depth

30 degrees 2 times the depth

45 degrees 1.4 times the depth.

For most work this is close enough.

[ January 17, 2006, 07:38 PM: Message edited by: iwire ]
 
Re: 3 phase motor questions

Originally posted by jbwhite:
iwire got it

30 deg offset is times two.

what is the shrink?
I would have to go to my Uglys book for that.

I usually run EMT so shrink is something I hardly ever worry about.
 
Re: 3 phase motor questions

I think this is a trick question, the original post said he is studying the NEC looking for the answers.
 
Re: 3 phase motor questions

That's an interesting point. When I first read the post I was a little unnerved but I wasn't sure why. Now I know. Why is the OP searching the NEC for information about how to use a single phase motor on a three phase system? The NEC isn't a how-to manual or a training manual. Are we sure this isn't a DIYer?

Bob
 
Re: 3 phase motor questions

Originally posted by bthielen:
That's an interesting point. When I first read the post I was a little unnerved but I wasn't sure why. Now I know. Why is the OP searching the NEC for information about how to use a single phase motor on a three phase system? The NEC isn't a how-to manual or a training manual. Are we sure this isn't a DIYer?

Bob
yo guys ..not to be cynical (is this the rite term ??)but, if he's an "apprentice" he should be attending some type of "Schooling" .. should ask your teacher ...

was just thinking ..you said before ..my lunch depends on this (I think) hhmmm ... don't hurt anyone ... especially your self ... M :cool:
 
Status
Not open for further replies.
Top