I am looking for some advice/references on a question that I thought I knew the answer to, but now I am second guessing myself.
I have a project with a 15hp 230/460v 3ph motor being installed on a subpanel. The MDP is about 200 feet away, and the motor is a 4 pole, 11.2 kW, has a 1.15 SF, NEMA code G and LRA of 256.53 amps at 208 volts (which is what it will be run at... the manufacturer ok'd the lower voltage for the motor already).
My question has to do with starter selection and if a soft start is required. The is no documentation for the MDP loads, however a data logger showed a max peak of 135 amps over a week long period and the MDP is fed by a 15 kVA xfmr about 15 feet from the MDP which is a 208/120 200 amp panel.
I was going to just run a DOL starter, but now I am wondering if I will cause any problems upstream of the motor. The MDP is feeding a mystery building that the client won't let me into to verify loads. It appears to be full of electronics equipment (based on an array of antenna I observed on the roof). It's a government facility; maybe they have the Obamacare website housed there... I dunno.....
Anyway; normally I would not expect the start current to present a problem upstream of the motor on a DOL, but now I am wondering about this mystery building and if I need to error on the side of safety due to unknown electronics present?
Any thoughts or advice?
Thanks,
I have a project with a 15hp 230/460v 3ph motor being installed on a subpanel. The MDP is about 200 feet away, and the motor is a 4 pole, 11.2 kW, has a 1.15 SF, NEMA code G and LRA of 256.53 amps at 208 volts (which is what it will be run at... the manufacturer ok'd the lower voltage for the motor already).
My question has to do with starter selection and if a soft start is required. The is no documentation for the MDP loads, however a data logger showed a max peak of 135 amps over a week long period and the MDP is fed by a 15 kVA xfmr about 15 feet from the MDP which is a 208/120 200 amp panel.
I was going to just run a DOL starter, but now I am wondering if I will cause any problems upstream of the motor. The MDP is feeding a mystery building that the client won't let me into to verify loads. It appears to be full of electronics equipment (based on an array of antenna I observed on the roof). It's a government facility; maybe they have the Obamacare website housed there... I dunno.....
Anyway; normally I would not expect the start current to present a problem upstream of the motor on a DOL, but now I am wondering about this mystery building and if I need to error on the side of safety due to unknown electronics present?
Any thoughts or advice?
Thanks,