Door is wide open for many possibilities with no more specifications than you give.
some key things -
supply volts
control volts - you did mention 120 volt coil, do we need to transform a control voltage from the supply volts or do you have separate control voltage source already?
Presuming since you called it a "starter" you will need motor overload protection incorporated into it - next comes what is motor current in order to make sure your overload will have settings within correct range and whether you need class 10, class 20, class 30 protection. Do you want one that has enhanced phase loss protection? Melting alloy, bimetallic, electronic?
Is there already a branch circuit supplying this, is it within site of the branch circuit device or other disconnecting means, or will you need maybe a combination starter with fused switch or breaker within it?
Then comes enclosure type necessary - NEMA 1, 3R, 4, 4X, 12, 13...