Looking for some thoughts on a 3 phase motor tripping the thermal. I have a coolant pump motor on a industrial machine that randomely trips the thermal motor protection. It's on an Australian built machine that operates on 415 volts nominal, the thermal protection is a Moeller PKZ MO -10. I checked the load on all three legs while I was on site and had readings that were consistent in the 6.2A range(+/- .2) The nameplate lists 6.6A . I can see a slight difference since the actual operating voltage is a bit different than the motor nameplate. I realize that this thermal is oversize and does need to be changed in order to properly protect (owner changed pumps awhile back and got a smaller pump). I did find some excessive arcing on one of the contacts inside the contactor. Could that possible interruption be enough to cause a single phasing occurance? Does the thermal function on the principle that when a phase is lost or interrupted the other legs amperage exceeds the setting and trips?Don't do alot with industrial applications, how forgiving is a thermal unit in a situation where intermittent arcing may occur as opposed to a total loss of the leg? Thanks for any help.