GeorgeB
ElectroHydraulics engineer (retired)
- Location
- Greenville SC
- Occupation
- Retired
I should be ashamed to ask this, but am very puzzled. I was helping a customer with hydraulic problems; numerous internal leaks warming a reservoir with about 4 kW of waste energy ... and they were having problems with the motor sometimes not starting. They blamed the pump since their electricals had been checked thoroughly. I blamed the 5.5 HP of extra-ordinary load at startup ... which was well under the 20 HP motor.
I'm told today that the problem was that they were single phasing.
I thought that a running motor would continue running at significant over-current on the 2 powered phases until something happened ... motor failure, overload trip, or fuse trip ... but that full power could not be delivered to the load. I still think that is true.
The confusion ... sometimes (at light load, for what it's worth), this 20 HP motor would start. After it started, we were pulling over 50% of rated power in our tests. No one looked at current.
This is a standard 460-3-60 motor started across the line. How can it start?
Thanks!