So I got involved with this job my company was doing today. The guys were providing some temp power for a bunch of RV's set up for a show. They daisy chained a few single phase temp panels with receptacles and cords off an existing 3 phase panel. Some breakers in the temp panels were tripping because some of the RV's were drawing more than they were told they would. So a few 120V temp cords were also ran from the 3 phase panels to power some of the trailers and motorhomes.
Here's the weird part: I'm going around amp clamping all the circuits to see if they are overloaded. I check the ground and see it has a bunch of current on it. I look around and see that the N and G are bonded in the temp panels. OK, that's wrong and explains the ground current. Then I check the neutral and, of course, it has a little more on it that the ground, which is incorrectly installed in parallel with the N. This is the part I don't get, the sum of the G and N currents exceeds the the current on either one of the hots! Apparently, the RV's have power inverters to run the lights that are 12V Dc, not sure if this makes a difference. I know the basic formula for calculating N current in a 3 phase system, but I don't know how power factor plays in. Could this make the N current exceed the line current? Going from memory, I was getting readings like: A: 9 amps. B: 19 amps C: not used N and G sum: 30 amps. These readings are taken on the temp feeder.
And here's the weirder part: Since I could not understand the excessive N current. I kept checking into this problem. I shut off the 2 pole breaker that feeds the temp panels and checked the N current on the temp feeder. It still read about 25 amps!! I am totally baffled were that current could be coming from. I did drop to zero when I shut off the main three phase panel however.
Any ideas?
Here's the weird part: I'm going around amp clamping all the circuits to see if they are overloaded. I check the ground and see it has a bunch of current on it. I look around and see that the N and G are bonded in the temp panels. OK, that's wrong and explains the ground current. Then I check the neutral and, of course, it has a little more on it that the ground, which is incorrectly installed in parallel with the N. This is the part I don't get, the sum of the G and N currents exceeds the the current on either one of the hots! Apparently, the RV's have power inverters to run the lights that are 12V Dc, not sure if this makes a difference. I know the basic formula for calculating N current in a 3 phase system, but I don't know how power factor plays in. Could this make the N current exceed the line current? Going from memory, I was getting readings like: A: 9 amps. B: 19 amps C: not used N and G sum: 30 amps. These readings are taken on the temp feeder.
And here's the weirder part: Since I could not understand the excessive N current. I kept checking into this problem. I shut off the 2 pole breaker that feeds the temp panels and checked the N current on the temp feeder. It still read about 25 amps!! I am totally baffled were that current could be coming from. I did drop to zero when I shut off the main three phase panel however.
Any ideas?