Have a scenario where we have 3-phase feeding a different building on a campus. The only loads in this building are 3-phase. Can anyone point me to where in the NEC it states that a neutral wire does or does not need to be ran to this outbuilding?
 
Have a scenario where we have 3-phase feeding a different building on a campus. The only loads in this building are 3-phase. Can anyone point me to where in the NEC it states that a neutral wire does or does not need to be ran to this outbuilding?
Will this be a feeder or separate service to the building?
 
Have a scenario where we have 3-phase feeding a different building on a campus. The only loads in this building are 3-phase. Can anyone point me to where in the NEC it states that a neutral wire does or does not need to be ran to this outbuilding?
See post #4

However, I would question why you wouldn't want the neutral/grounded conductor present at the building. You probably would want lights, or general purpose receptacles. Even if you don't want/need them now, there's always future needs. One more conductor can't be that much more.
 
See post #4

However, I would question why you wouldn't want the neutral/grounded conductor present at the building. You probably would want lights, or general purpose receptacles. Even if you don't want/need them now, there's always future needs. One more conductor can't be that much more.
I cursed more than one EC, EE, Owner that thought it was cheaper to leave it out.
 
I have seen it done with 240V pump stations when feeders were up-sized neutral was omitted so existing duct could be used the alternative was a huge trenching project ... it adds some complexity but if saves cost..
Its easier than ever to get 100-240V LED lighting than can be run L-L, but you have to switch both poles which adds some complexity if your using a photo eye etc. The required 120v GFCI by the panel can be on a small transformer.
 