People have been asking for a picture so here it is
3 phase ungrounded 300kva delta delta pad mounted transformer 4800 volt primary and 480 volt secondary to first disconnect 3/0 secondary feeders
Goes to gutter at another building to allow tap to both a 3 phase ungrounded distribution panel to power motors and other tap within gutter to single phase disconnect 200 amperes selected by boss from phases A and C
1 phase disconnect 200 ampere breaker boss selected feeds single phase 50 KVA 480 v to 240 v secondary with 3/0 wires boss selected to feed single phase distribution panel. Neutral is for the first time now derived from single 50kva transformer
What happens to derived neutral and system bonding jumper?
Does this transformer get a system bonding jumper installed with a supply side bonding jumper to 1 phase panel or does single phase distribution panel get a system bonding jumper as the first point of disconnect? (bonding neutral conductor derived from transformer to single phase distribution panel neutral bus, EGC, case and grounding conductor?
Doing the latter will also connect grounded conductor to 3 phase panel that is bonded with gutter
3 phase ungrounded 300kva delta delta pad mounted transformer 4800 volt primary and 480 volt secondary to first disconnect 3/0 secondary feeders
Goes to gutter at another building to allow tap to both a 3 phase ungrounded distribution panel to power motors and other tap within gutter to single phase disconnect 200 amperes selected by boss from phases A and C
1 phase disconnect 200 ampere breaker boss selected feeds single phase 50 KVA 480 v to 240 v secondary with 3/0 wires boss selected to feed single phase distribution panel. Neutral is for the first time now derived from single 50kva transformer
What happens to derived neutral and system bonding jumper?
Does this transformer get a system bonding jumper installed with a supply side bonding jumper to 1 phase panel or does single phase distribution panel get a system bonding jumper as the first point of disconnect? (bonding neutral conductor derived from transformer to single phase distribution panel neutral bus, EGC, case and grounding conductor?
Doing the latter will also connect grounded conductor to 3 phase panel that is bonded with gutter