We have a 30KVA, 480 volt Delta primary to 208Y 120 secondary transformer feeding a 3 phase breaker panel
We have one fixed appliance unit requiring a 3 phase 220 volts source (which transformer was stepped up to 220 volts from transformer taps). All other loads are single phase being fed from individual 1 of 3 phases and a neutral derived from transformer XO terminal to 3 phase panel neutral buss (later to be tied in with ground buss as first point of disconnect)
Can anyone refer me to NEC code which would stipulate this as a violation, such as 3 phase panels having to supply 3 phase loads and single phase panels supplying single phase loads?
My coworker says this is not a violation
Also would system bonding jumper be installed in first point of disconnect 3 phase panel or in transformer? Thanks
We have one fixed appliance unit requiring a 3 phase 220 volts source (which transformer was stepped up to 220 volts from transformer taps). All other loads are single phase being fed from individual 1 of 3 phases and a neutral derived from transformer XO terminal to 3 phase panel neutral buss (later to be tied in with ground buss as first point of disconnect)