my journeyman told me that with a 100amp 3phase panel you can have 240amps, his reasoning, 100a x 3phases=300a, 300a x .80 adjustment = 240a. thats not right is it.
if i use #2 copper out of the 75degree colomn gives me 115 amps to work with and then multiply that by 80% for 4 current carrying conductors gives me a final ampacity of 92 amps for #2 copper. i can then use a 100amp breaker to service a load of 92 amps. all the loads will be single phase loads. anyone have some input
if i use #2 copper out of the 75degree colomn gives me 115 amps to work with and then multiply that by 80% for 4 current carrying conductors gives me a final ampacity of 92 amps for #2 copper. i can then use a 100amp breaker to service a load of 92 amps. all the loads will be single phase loads. anyone have some input