Hello,
To start, I would like to state that I am a GC, not an electrician. We are working on an apartment remodel and found a situation where the there is no ground. It is an old style, two wire building where all the plugs had been changed to three holes (without any grounding). The panel is 3 phase because the old HVAC air handler ran on 3 phase power. There is no way to provide a mechanical ground.
The existing solid copper wiring is in bad shape (we found some outlets jumped with speaker wire laid under tile). Some of the existing EMT is usable but a lot is not; some wires are just stuck in the conduits and there is no way to get them to move. The easiest option is to run new conduit along the ceiling (all concrete construction) and cover it with a gypsum false ceiling. I was reading through the NEC and cannot decide what the proper conduit would be (we even considered NMC without conduits).
It seems that ungrounded and unbonded EMT is just a bead idea, which leaves PVC for the new runs. That seems fine since the ceiling space shouldn't be subject to physical damage (though not sure 1/2" gypsum is really much protection). I also suggested to the electrician that we change the panel and add GFCI/AFCI combo breakers.
Any feedback on this solution would be appreciated. Does the PVC conduit (back to the main panel, where they're being replaced) with GFCI/AFCI breakers and stranded copper wire seem like the best solution in this scenario? Normally I would just let the electrician do his thing, but I thought I would ask since I don't see an ideal solution here.
Thank you.
To start, I would like to state that I am a GC, not an electrician. We are working on an apartment remodel and found a situation where the there is no ground. It is an old style, two wire building where all the plugs had been changed to three holes (without any grounding). The panel is 3 phase because the old HVAC air handler ran on 3 phase power. There is no way to provide a mechanical ground.
The existing solid copper wiring is in bad shape (we found some outlets jumped with speaker wire laid under tile). Some of the existing EMT is usable but a lot is not; some wires are just stuck in the conduits and there is no way to get them to move. The easiest option is to run new conduit along the ceiling (all concrete construction) and cover it with a gypsum false ceiling. I was reading through the NEC and cannot decide what the proper conduit would be (we even considered NMC without conduits).
It seems that ungrounded and unbonded EMT is just a bead idea, which leaves PVC for the new runs. That seems fine since the ceiling space shouldn't be subject to physical damage (though not sure 1/2" gypsum is really much protection). I also suggested to the electrician that we change the panel and add GFCI/AFCI combo breakers.
Any feedback on this solution would be appreciated. Does the PVC conduit (back to the main panel, where they're being replaced) with GFCI/AFCI breakers and stranded copper wire seem like the best solution in this scenario? Normally I would just let the electrician do his thing, but I thought I would ask since I don't see an ideal solution here.
Thank you.