I had a question asked to me and could not think of an answer.
If you are feeding a 3 phase 120/208V pump at 400' from feed. Can you use different size wire to feed it?
i.e use a 4/0 4/0 2/0 with a 250 MCM single
What is the problem with doing this? any voltage/amperage issues?
I'm not grasping what the heck you are talking about here in the bold text.
I'm also not sure you understand what you have. A 3 phase motor is NOT "120/208", it is 208V. The 120V is for phase to NEUTRAL loads, the motor does
not use the Neutral, so you don't run a neutral wire to it.
...That will lead to a larger percentage difference in current between the three windings and could potentially lead to overloading one or more of the windings without the motor's overloads detecting the condition. It could also cause the motor to run less efficiently.
I wholeheartedly agree. Even a slight phase
voltage imbalance leads to
a lot more current imbalance and the creation of negative sequence currents flowing in the motor, which leads to negative torque in the rotor, resulting in 2 of the phases "fighting" the third to keep the motor spinning. More of the current that is flowing in the circuit is going toward heating than it should, but the OL relay will only see the total and the trip point is based on that being EVEN across the phases. So what can happen is that even if the current is below the trip threshold of the OL relay, the THERMAL EFFECT of that unbalanced current on the motor is as if the motor WAS overloaded, continuously, and yet the OL will not protect it.
I've seen if happen where there was just a significant difference in the length of one cable, which changed the circuit resistance in that one phase (someone didn't want to cut the cable for fear they would "waste" it) and burned up a 500HP motor, yet the OL relay never tripped because the current never exceeded the FLA.
In this case you would have (presumably) 2 phases with 4/0 cable that has a resistance of .049ohms/1000', so a total resistance of .0196ohms, and one phase of 2/0 cable with a resistance of 0.078ohms/1000' so a total resistance of .0312ohms, over 1-1/2 times as much resistance. It will make a difference in the current balance. If the motor is never loaded to more than 50% of it's rating you may never know the difference, but if the motor is loaded to 98% of it's rating you may lose the motor. Where the line is going to end up is difficult to predict, so the safe bet is to just use the same size cable for all 3 phases and not worry about it.