Yes, #6 THHN is rated for 75 amps. But 60 amps would be 80% of 75. So it's possible that was done on purpose depending on the continuous load that was on it.

Jason
 
Yes, #6 THHN is rated for 75 amps. But 60 amps would be 80% of 75. So it's possible that was done on purpose depending on the continuous load that was on it.

Jason
termination rating is likely going to be 75C which will limit ampacity to 65 amps.

As long as 100% of non-continuous load plus 125% of continuous load is not more then 65 amps you can protect 6 AWG with a 70 amp breaker. If the calculation comes to 66 amps you can still use the 70 amp breaker but will need to increase conductor to 4 AWG.

Now if your load is motor(s) you possibly see 90-125 amp breaker on 6 AWG in some instances, but the rules change for motors.
 