I have a service rated 480V 200A. I have a piece of 3-phase equipment that draws 400A of 3-phase power at 208V. I want to put in a 3-phase transformer to get 208 from the 480. My calculation is as follows (ignoring transformer losses and assuming a balanced load):
480V 3P @200A = 166kVA
208V 3P @400A = 144kVA
therefore the 200A 480V service has enough power.
I consulted with an electrician, and his response was "Not enough power. 208 X 400 =83,200 / 360=231".
It sort of looks like he's converting the 400A load to kVA as if it were single-phase, and then converting that back to 3-phase current, but it just doesn't seem right to me. Maybe I'm missing something.
Would appreciate any clarification/edification, thanks.