3 Phase Short Circuit Current

Status
Not open for further replies.

big john

Senior Member
Location
Portland, ME
When calculating SCC on a 3 phase transformer all the equations seem to be:

(kVA * 1000) / (V * 1.732)

This results in less than the current on a single phase 480V fault.

What is happening that is necessary to calculate the square-root of 3 into this fault current?
 

Ingenieur

Senior Member
Location
Earth
I know, I'm just asking about the 1.732 part of calculating FLA.

because it is 3 ph, correct?

S va = sqrt3 x v (l-l) x i (line)

a 3 ph 1000 kva xfmr is 3 x 333.3 kva xfmrs
so the 'single ph' i is 333300/480
3 ph is 3 x 333300 / (1.732 x 480)
 

big john

Senior Member
Location
Portland, ME
But if the fault is L-L, then it more than one winding would be contributing power.

That's why I don't follow the point of the single winding calculation.
 

Ingenieur

Senior Member
Location
Earth
But if the fault is L-L, then it more than one winding would be contributing power.

That's why I don't follow the point of the single winding calculation.

you can't compare a 1000 3 ph with a 1000 1 ph

you are correct 2 x 333.3 kva would contribute
but they are not in ph so the Z/coil does not simply sum

it's times like this I wish I had video and a chalk board lol

3 ph 277/480 wye 1 MVA
let's assume each coil has Z = 0.01152 Ohm (pu 5%)
line-line involves 2 coils
but not 2 x 0.0115 = 0.02304
but 2 x sin120 x 0.01152 = 0.01995

so fault = 480/0.01995 = 24,060 A
same as 100000/(1.732 480 0.05) = 24.060 A
identical

1 ph 480 666667 va ( same capacity as the 3 ph)
same pu 5% so Z = 0.01728 for the single coil

fault = 480/0.01728 = 27,778 A
a bit more
 

Ingenieur

Senior Member
Location
Earth
One more step
assume rated current is the same for both the 1 ph and 3 ph xfmrs
3 ph 1 MVA 277/480 wye 1203 A
1 ph kva = 480 x 1203 = 577,350
pu for both is 5%

the 3 ph fault remains 24,060 A

For the new 1 ph
Z = 0.05 x 480^2/577350 = 0.020
fault = 480/0.020 = 24,060 A
same as 3 ph
 

big john

Senior Member
Location
Portland, ME
So if I'm understanding this right, the short answer is that even though power goes up by 1.732, the series winding impedance increases by the same value, effectively making it like only 1 winding is contributing fault current?
 

Ingenieur

Senior Member
Location
Earth
So if I'm understanding this right, the short answer is that even though power goes up by 1.732, the series winding impedance increases by the same value, effectively making it like only 1 winding is contributing fault current?


Assuming the current rating (not power) is the same you could have a 1 ph with low pu Z and a 3 ph with high Z

so the the phase fault on the 1 ph could be larger

you can't draw a fixed relationship between 1 ph and 3 ph xfmr faults
you could I guess, but it would an algebraic expression based on (for a common v)
pu Z's
kva
 

big john

Senior Member
Location
Portland, ME
You can't draw a fixed relationship between 1 ph and 3 ph xfmr faults
But isn't that what the original equation is doing, that's why we multiply by 1.732?

If I have a 1kVA 277V transformer with a 5% individual impedance, then I've got a SCC of 72A. (1000VA/277V/0.05Z)

But if I gang three of those then I've got a 3kVA 480V with a total 5% impedance and it gives me a SCC of 72A (3000VA/480V/[0.05Z*1.732])

Does that work?
 

Ingenieur

Senior Member
Location
Earth
But isn't that what the original equation is doing, that's why we multiply by 1.732?

If I have a 1kVA 277V transformer with a 5% individual impedance, then I've got a SCC of 72A. (1000VA/277V/0.05Z)

But if I gang three of those then I've got a 3kVA 480V with a total 5% impedance and it gives me a SCC of 72A (3000VA/480V/[0.05Z*1.732])

Does that work?


We mult by sqrt3 because we have 3 signals offset by 120 deg

Yes that works for the i to be equal
as long as
kva 1 ph = 1/3 kva 3 ph
v 1 ph = vl-l 3 ph / sqrt3
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
The short-circuit current [supertransient, transient and steady state] is as following:
single phase Isc1=sqrt(3)*VLL/(X1 +X2+Xo)
phase-to-phase Isc2=VLL/(X1+X2)
three phase : Isc3=VLL/sqrt(3)/(X1)
If Xo~0 and X1=X2 [far from generator] then Isc1/Isc2=1.5
If Xo~X1 and X1=X2 [far from generator] then Isc1/Isc2=1
If Xo>X1 Isc1/Isc3<1
 