3 phase to single phase supply
nagasahitya
New member
India
Hiii ,
I require a single phase ac supply in my LAB with volatge rating (1000 V)rms ,current rating 600 A. 3 phase 415v supply is available in my LAB.please tell me the best methods to convert my 3 phase supply in to single phase.Important thing is i must maintain balanced load on the 3 phase side.
Regards
sahitya
ggunn
Austin, TX, USA
Hiii ,
Regards
sahitya
There is no way that I know of to make single phase from three phase using all three phases.
Ingenieur
Earth
1000 VAC x 600 A = 600 kva
input at 415/3 is 835 A
600 kva 415:1000 3 ph xfmr
feeding a 1000 VAC 1000+ HP VFD (expensive VFD lol), 1000 vac is a common mining voltage and drives are available
use two phase legs of the output
input will be balanced since rectified to a DC bus
GoldDigger
Placerville, CA, USA
Retired PV System Designer
Just such a transformer connection has been described in a thread here. It produces single phase drawing equally from all three source phase lines.
Ingenieur
Earth
the common way with xfmrs is a 2 winding primary open delta and a 2 series winding secondary
but it is not balanced
2 phases are equal, the third is 1/2 the load iirc
I'd like to see how it is done balanced
3 phase primary coupled to a single sec coil?
here's the post that purports to get 3 ph-1 ph balanced operation no drawings or real info though http://forums.mikeholt.com/showthread.php?t=146298
LMAO
Texas
use the 3 phase to feed a VFD with a sinewave filter at it output because VFD output is not sinusoidal. Needless to say, it is not straightforward, you need professional engineers to do all the design.
gar
Ann Arbor, Michigan
EE
160518-1319 EDT
A transformer method is based on the mathematical identity that the sum of multiple sine waves of identical frequency and phase locked together produces a single sine wave of the same frequency, and some phase angle.
If A to N is 120 V, B to N is 240 V, and C to N is 240 V, then by properly connecting these secondaries in series, they are not joined at a neutral point, the summed voltage is 240 V and in phase with A to N The real power loading on each transformer is the same. Thus, a balanced real power load is presented to the source.
Ingenieur
Earth
160518-1319 EDT
3 sec coils
ph A 120/0
ph B 240/120
ph C 240/-120
series connected
how are the 'dots' oriented?
A and B the same, C opposite?
all the same?
etc
if in series all carry the same current, correct?
but if the V is different (120 and 240) the power must be different per coil?
ggunn
Austin, TX, USA
I only remember some unsubstantiated claims that it is possible.
gar
Ann Arbor, Michigan
EE
don_resqcapt19
Illinois
retired electrician
It would be the same connection that you use on a 12 lead generator....a double delta or a zig zag connection of the secondary side, however you would need the secondary side of each of the 3 transformers to have all 4 leads brought out.
mbrooke
Batteries Included
United States
Technician
GoldDigger
It is not a simple as three primaries and one secondary.
Basically you interwire three individual secondary windings in a complicated way. It is similar to the complicated interconnection of the Scott T circuit between two phase and three phase.