- Wisconsin
- PE (Retired) - Power Systems
There is no line side N connection at the buck-boost transformer, it is at the beginning of the 208Y/120 system where the 'line side' neutral to ground bonding occurs.Jim, if memory serves me this is your area of expertise, so please forgive me, but I cannot find anything in code that makes such a statement (Edit to add: requiring the line-side neutral connection). ....
This is a single-phase transformer connected across two phases of a 3-phase system, which creates a separately derived single-phase 120/240 volt system, and as such, it would require ground neutral bonding on the load-side.
Not only would requiring the line-side neutral completely negate the possibility of creating a 120/240 volt separately derived system, but part of me thinks this could create problems with a grounded conductor on both sides of a transformer, and each of them having their own grounding electrode system.
If I am off base, can you tell me which section of code I should read?
At the start of the feeder circuit we have 208V L-L & 120V L-G, therefore at the 'line side' of the buck-boost transformer we must also have 208V L-L and 120 L-G. Now we must ground the neutral of the 'load side' 240V side per the NEC, and the now grounded neutral is common to both the line and load sides. So if the 'line side' is 208/120 how can the secondary also be 240/120?
An autotransformer (i.e. buck-boost) is not a separately derived system.