Most utility companies install three phase meters these days. They do this reguardless if your service is going to be single phase or three phase. But I don't reccomend doing what your are doing. First of all, why? three phase power is more efficient than single phase. What your doing is unbalancing your three phase power to make it less efficient. Your also gonna create a current across your neutral, by unbalancing the phases. That is the lost energy that u will be wasting. U should call the utility company and have them change your service to single phase, they generally do this with no charge involved. But I am worried about why u are doing this? Did your overall load in your house change? If it did not, and you are going to use one less leg for the house load, you will be increasing the ampacity of the other two legs you are using because you have eliminated one leg. That could be dangerous based on how they are sized.