Originally posted by jim dungar: Conductors are sized based on their loads. Branch circuit overcurrent protective devices are sized based on the wire. Transformer OCPDs are sized based on the transformer.
All well and good. But it does not quite answer the question that I think theshockdoc is asking. I say that because the same question has been nagging at me.
Consider the following scenario. I hope I have all the numbers right. It involves a 480 ? 120/208Y transformer.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">We calculate the load on a panel to be 36 KVA. At 208 volts this equates to 100 amps. Reflected to the primary side, this equates to 43 amps.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">We select a 45 KVA transformer. Rated primary current = 54 amps. Secondary rated current = 125 amps.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">We select the primary OCPD at 125 amps (just under 250% of XFMR rating).</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">We select the secondary OCPD at 150 amps (just under 125% of XFMR rating).</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">For the primary feeder, we select a #6 copper. Ampacity at 60C is 55 amps. This exceeds the calculated load, and is just slightly over the rated primary current.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> Now we postulate a high-impedance fault on the secondary side. We could instead postulate that the owner installs more load. In either case, let us say that the load, as seen by the primary side, has increased to 65 amps. This is an 18 % overload on the transformer.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The secondary OCPD will not trip, as this load is exactly equal to the selected OCPD rating.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The primary OCPD will not trip, as this load is far less than 250% of the primary rated current.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, no protective device will act to terminate this event.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The transformer will not be at serious risk, as it can handle an 18% overload for an extended time, with no greater impact than a reduction in its useful lifetime.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">But the primary feeder conductors will see 18% more than their rated ampacity. They will not be able to maintain this condition indefinitely. They will overheat, and may even cause a fire.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Back to the original question: Why is it acceptable to leave the primary conductors with insufficient protection?