GotShocked
Member
- Location
- Richland, WA, Benton County
I should know this but when you have a 3 phase bank of single phase transformers, are the individual transformer impedances summed to provide the 3 phase impedance?
No. You can use the average. If calculating worst case 1phase fault, use the smallest if you want to be conservative. A matrix solution will allow you to use all three.I should know this but when you have a 3 phase bank of single phase transformers, are the individual transformer impedances summed to provide the 3 phase impedance?
I would run the calcs separately. For most 1 phase, use the impedance of the lighting pot, but also consider the 1-phase faults that involve the high leg pot. For 3-phase, you can account for the open delta with the correct formulas but for a scratch calc you could blend.How about an open delta with one transformer larger then the other?
My guess is higher impedance on the high leg only, otherwise for figuring maximum available fault current (which is what most of us need to know the impedance for) I have always just used the impedance of the larger unit, if anything it may yield a little higher max fault current then actual available current in certain situations.
Yes, just like you would add the individual kVA for individual phases if they were singles to equate to a 3 phase.
Correction to my last post, the bank impedance is 2.2%, correct?
[FONT=Courier New]
#1: Same % Z
#2: Lighting pot (AB) is Z/2
#3: Lighting pot (AB) is 2*Z
#4: Same % Z, lighting pot (AB) is 2*kVA
#5: Same % Z, BC open
#6: Same % Z, lighting pot (AB) is 2*kVA, BC open
#1 #2 #3 #4 #5 #6
ABC fault ABC fault ABC fault ABC fault ABC fault ABC fault
A 3.590 kA A 5.465 kA A 2.735 kA A 5.465 kA A 3.590 kA A 5.426 kA
B 3.590 kA B 5.490 kA B 2.747 kA B 5.490 kA B 2.036 kA B 4.061 kA
C 3.590 kA C 3.590 kA C 3.590 kA C 3.590 kA C 2.104 kA C 2.140 kA
A-N Fault A-N Fault A-N Fault A-N Fault A-N Fault A-N Fault
A 3.553 kA A 6.373 kA A 2.072 kA A 6.372 kA A 2.760 kA A 5.511 kA
N 3.553 kA N 6.373 kA N 2.072 kA N 6.372 kA N 2.760 kA N 5.511 kA
B-N Fault B-N Fault B-N Fault B-N Fault B-N Fault B-N Fault
B 3.553 kA B 6.373 kA B 2.072 kA B 6.372 kA B 2.760 kA B 5.511 kA
N 3.553 kA N 6.373 kA N 2.072 kA N 6.372 kA N 2.760 kA N 5.511 kA
C-N Fault C-N Fault C-N Fault C-N Fault C-N Fault C-N Fault
C 2.872 kA C 3.191 kA C 2.393 kA C 3.191 kA C 1.301 kA C 1.505 kA
N 2.872 kA N 3.191 kA N 2.393 kA N 3.191 kA N 1.301 kA N 1.505 kA
A-B Fault A-B Fault A-B Fault A-B Fault A-B Fault A-B Fault
A 3.109 kA A 5.175 kA A 2.071 kA A 5.175 kA A 2.068 kA A 4.127 kA
B 3.109 kA B 5.175 kA B 2.071 kA B 5.175 kA B 2.068 kA B 4.127 kA
A-C Fault A-C Fault A-C Fault A-C Fault A-C Fault A-C Fault
A 3.109 kA A 3.454 kA A 2.763 kA A 3.454 kA A 2.068 kA A 2.068 kA
C 3.109 kA C 3.454 kA C 2.763 kA C 3.454 kA C 2.068 kA C 2.068 kA
B-C Fault B-C Fault B-C Fault B-C Fault B-C Fault B-C Fault
B 3.109 kA B 3.454 kA B 2.763 kA B 3.454 kA B 1.032 kA B 1.373 kA
C 3.109 kA C 3.454 kA C 2.763 kA C 3.454 kA C 1.032 kA C 1.373 kA[/FONT]