I'm working on a restaurant that has 2 services. One is a new 240/120 1ph. I just installed.
When I was tracing out all the existing circuits to label the new service, I noticed all the receptacles on the 2nd service were reading "Open Ground"
The 2nd service is an old 240v 3ph. corner grounded supply. That service is used to supply a customer owned 208Y/120 3ph transformer
That transformer supplies a 3 phase switchboard. I checked in the transformer and in the switchboard and there is no bonding between ground and neutral.
The transformer case is bonded to the 240v service and has an additional ground bar connected to the case.
The ground wire runs through the transformer to the ground bar in the switchboard.
Obviously one of the 240v service phases is connected to ground w/ two rods and CWpipe.
I had already replaced all the ground clamp connections on the 240v panel as they were corroded.
In the 208Y/120v switchboard I'm reading phase to ground voltages of A-55v / B-44v / C-55v.
Phases to neutral are all good at 120v
Phase to Phase are all good at 212v
Shouldn't there be bonding jumper between neutral and ground somewhere?
Not much 3 ph experience and 1st corner grounded service I've seen in 40 years. I don't want to do anything stupid!
When I was tracing out all the existing circuits to label the new service, I noticed all the receptacles on the 2nd service were reading "Open Ground"
The 2nd service is an old 240v 3ph. corner grounded supply. That service is used to supply a customer owned 208Y/120 3ph transformer
That transformer supplies a 3 phase switchboard. I checked in the transformer and in the switchboard and there is no bonding between ground and neutral.
The transformer case is bonded to the 240v service and has an additional ground bar connected to the case.
The ground wire runs through the transformer to the ground bar in the switchboard.
Obviously one of the 240v service phases is connected to ground w/ two rods and CWpipe.
I had already replaced all the ground clamp connections on the 240v panel as they were corroded.
In the 208Y/120v switchboard I'm reading phase to ground voltages of A-55v / B-44v / C-55v.
Phases to neutral are all good at 120v
Phase to Phase are all good at 212v
Shouldn't there be bonding jumper between neutral and ground somewhere?
Not much 3 ph experience and 1st corner grounded service I've seen in 40 years. I don't want to do anything stupid!