Just pick one of those up at........where? You tell me and I will get a sackful of them.Use 100% rated cb in order not to deal with 1.25 factor
Sent from my Nexus 5 using Tapatalk
A customer has a 75kva 3 phase transformer. The customer wants to input 100 amps at 208v 3 phase and the secondary would be 480v 3 phase. How many amps will be available on the secondary side at 480v?
If the main 480V is from a MV/480V DY the corner grounding of the 2nd back feed transformer is out of the question
Second thing is this a transformer designed for step down and you wish to "back feed" it or is it a step up transformer? 2014 added wording that effects use of a "back feed" transformer, does not prohibit it but says something to the effect it must be designed to do that.
You probably still find the high voltage side is delta connected and has no neutral unless it was intended to be a step up transformer, then the low voltage side may be delta with no neutral.I think you will find that the dry type transformers being installed today are no longer labeled primary and secondary but high voltage and low voltage. Feed them either direction with out a code issue.
You probably still find the high voltage side is delta connected and has no neutral unless it was intended to be a step up transformer, then the low voltage side may be delta with no neutral.
The way OP is stated this may be an older transformer customer just has laying around and they want to know what they can run with it. If buying a new transformer you usually figure out the load needs then select a suitable transformer. Also trying to reinforce the idea that there is a good chance there is no neutral to the high voltage side of the transformer.And the enclosures may be painted gray but I don't see how either of those issues has to do with the code section you mentioned.
The only power requirement I have is that the transformer needs to be supplied with 100 amps at 208v. We will not be pulling a neutral just 3 phase. Transformer is a "custom built drive isolation transformer". Spec says "75kva 120/240/480 to 480Y/277 volt. Does this information help?
Can this be used with 208v? What is the end result if we feed with 208v?