We have a 75KVA ventilated dry transformer that needs set temporarily. It will supply 2 machines for a bit until separate transformers and load center are installed.
The primary per the 75KVA, will need protected at 90A/480V. Because the secondary side will feed two machines, there is no intention to run both machines at the same time right now. However, I want to ensure the transformer is well protected and I would prefer to have secondary current protection but with two machines connected, that is really not possible without a load center. Is primary protection plenty sufficient?
As well, we will probably need to install this transformer outdoors. We intend to shield it from radiant sun heating and weather with a small roof but want to ensure that is sufficient?
This is an Acme brand floor mount transformer if that helps.
Obviously wiring will be sized appropriate to the loads.
The primary per the 75KVA, will need protected at 90A/480V. Because the secondary side will feed two machines, there is no intention to run both machines at the same time right now. However, I want to ensure the transformer is well protected and I would prefer to have secondary current protection but with two machines connected, that is really not possible without a load center. Is primary protection plenty sufficient?
As well, we will probably need to install this transformer outdoors. We intend to shield it from radiant sun heating and weather with a small roof but want to ensure that is sufficient?
This is an Acme brand floor mount transformer if that helps.
Obviously wiring will be sized appropriate to the loads.