3 Phase Transformer feeding Single Phase

Status
Not open for further replies.

BPoindexter

Inactive, Email Never Verified
Location
MT Vernon, WA
I have an installation i was asked to look at. It is for some temporary job trailers. Two trailers rated for a 200A service each are being supplied from a single 3 phase delta-wye transformer rated at 150 KVA. One supply is connected to A Phase, B Phase and the XO while the other is connected to B Phase, C Phase, and the XO. Each one has 200A fuses. So in essence they have 1-200A fues on A, 2-200 fuses on B, and 1- 200A fuse on C. This does not appear to be correct to me. Am I missing something?
 
It may be fine as far as the NEC.

112.5 kva at 208 volts is about 312 amps. We can bring that up 125% which gets us to 390 amps. We are then allowed to roll up to the next standard size which would be a 400. When using multiple over current devices the total of those cannot exceed the ampacity of a single device.

So two 200s seems OK.
 
Also, ignoring power factor for the moment, two independent 200A line to line resistive loads will only generate a current of 200 x 1.73 amps in the common line conductor.
 