RyanMP1011
Member
- Location
- Texas, United States
- Occupation
- Industrial Electrician
Hey all,
I'm having this weird concern with a 480V Ungrounded Delta Secondary. With all loads removed, I read about 500V line-to-line, but the line-to-ground readings were:
A to Ground — ~1000V
B to Ground — ~1000V
C to Ground — ~700V
I tested these voltages with a Fluke T6 and a Fluke 87
Once the main breaker is turned on, there are 3 ground-fault indicator lamps that come on. A and C are brightly lit, while B is on, but very dim. Taking line-to-ground readings at this point shows:
A to Ground — ~350V
B to Ground — ~170V
C to Ground — ~350V
I tested these with a Fluke T6 and 87, as well as a solenoid meter.
Unknown primary voltage, but I believe it is no less than 12kV and no more than 15kV
Is this something to be concerned about?
If any more information is needed, let me know.
Thanks in advance.
I'm having this weird concern with a 480V Ungrounded Delta Secondary. With all loads removed, I read about 500V line-to-line, but the line-to-ground readings were:
A to Ground — ~1000V
B to Ground — ~1000V
C to Ground — ~700V
I tested these voltages with a Fluke T6 and a Fluke 87
Once the main breaker is turned on, there are 3 ground-fault indicator lamps that come on. A and C are brightly lit, while B is on, but very dim. Taking line-to-ground readings at this point shows:
A to Ground — ~350V
B to Ground — ~170V
C to Ground — ~350V
I tested these with a Fluke T6 and 87, as well as a solenoid meter.
Unknown primary voltage, but I believe it is no less than 12kV and no more than 15kV
Is this something to be concerned about?
If any more information is needed, let me know.
Thanks in advance.