3-Phase utility tied inverter feeding single phase load

Status
Not open for further replies.

philly

Senior Member
Trying to wrap my head around the following concept and am not quite seeing it. Hoping others can shed some light.

Hypothetical scenario....I have a 480/277 utility transformer feeding facility (lets say 100kVA for simplicity) and on secondary of transformer I have a 480V bus. On 480V bus I have (2) bi-directional AC/DC power supplies. The DC side of each power supply is connected through common DC bus.

The first power supply (#1) is connected L-N at 277V and draws current as a load from the 480V bus. The second power supply (#2) is a 3-phase connection to the 480V bus and circulates power back onto the 480V bus from supply #1. So power supply is 480V Bus >>supply #1 >> DC Bus ->>supply #2>>back to 480 bus and then circulating back over to input of supply #1.

My question is what happens to the 3-phase AC current that is being supplied from supply #2 and circulates back on to 480V bus with only a single phase load at input of supply #1. I know the neutral of the utility transformer will allow 3-phase inverter to connect to common 480V bus with L-N load at supply #1 being supported by transformer neutral but i'm having a hard time envisioning current flow?
 
... My question is what happens to the 3-phase AC current that is being supplied from supply #2 and circulates back on to 480V bus with only a single phase load at input of supply #1. I know the neutral of the utility transformer will allow 3-phase inverter to connect to common 480V bus with L-N load at supply #1 being supported by transformer neutral but i'm having a hard time envisioning current flow?
Lets assume the supplies are 100% efficient and all of the DC current out of supply #1 is drawn by the DC side of supply #2 (i.e., no net current onto the DC bus). Also the PF of supplies is unity. It seems in your example that there'll be no net circulation, but instead a power transfer from the output of the 480 line conductor and neutral that's loaded by supply #1 over to the other two 480 lines which drive the utility.

Say that supply #1 is drawing an input current I from the phase A and neutral of the 480 bus. Then supply #2 will drive each of the phases A, B, and C with a current 1/3 I . Therefore the net current drawn from the utility on phase A will be 2/3 I, and supply #2 will drive the utility with 1/3 I on phases B and C. The current on the neutral will be I .
Overall there will be very unbalanced "loading" between the phases as seen by the utility because the current will be in-phase with the voltage on phase A like with a resistive load, but at 180° on phases B and C because they are being driven with currents from supply #2 (although with half the current on phase A).
 