Trying to wrap my head around the following concept and am not quite seeing it. Hoping others can shed some light.
Hypothetical scenario....I have a 480/277 utility transformer feeding facility (lets say 100kVA for simplicity) and on secondary of transformer I have a 480V bus. On 480V bus I have (2) bi-directional AC/DC power supplies. The DC side of each power supply is connected through common DC bus.
The first power supply (#1) is connected L-N at 277V and draws current as a load from the 480V bus. The second power supply (#2) is a 3-phase connection to the 480V bus and circulates power back onto the 480V bus from supply #1. So power supply is 480V Bus >>supply #1 >> DC Bus ->>supply #2>>back to 480 bus and then circulating back over to input of supply #1.
My question is what happens to the 3-phase AC current that is being supplied from supply #2 and circulates back on to 480V bus with only a single phase load at input of supply #1. I know the neutral of the utility transformer will allow 3-phase inverter to connect to common 480V bus with L-N load at supply #1 being supported by transformer neutral but i'm having a hard time envisioning current flow?
Hypothetical scenario....I have a 480/277 utility transformer feeding facility (lets say 100kVA for simplicity) and on secondary of transformer I have a 480V bus. On 480V bus I have (2) bi-directional AC/DC power supplies. The DC side of each power supply is connected through common DC bus.
The first power supply (#1) is connected L-N at 277V and draws current as a load from the 480V bus. The second power supply (#2) is a 3-phase connection to the 480V bus and circulates power back onto the 480V bus from supply #1. So power supply is 480V Bus >>supply #1 >> DC Bus ->>supply #2>>back to 480 bus and then circulating back over to input of supply #1.
My question is what happens to the 3-phase AC current that is being supplied from supply #2 and circulates back on to 480V bus with only a single phase load at input of supply #1. I know the neutral of the utility transformer will allow 3-phase inverter to connect to common 480V bus with L-N load at supply #1 being supported by transformer neutral but i'm having a hard time envisioning current flow?