guilbertj2006
New member
- Location
- Pompano Beach, FL, USA
A 3-phase 480V HVAC compressor, with a nameplate RLA of 50A, tripped an interlocked 68A 3-pole CB. A megohm reading showed some deterioration on the stator insulation. (The compressor had been replaced in January 2012.) I took these readings: A to B: 477V. A to C: 477V. B to C: 461V. Amperage: A: 52A. B: 50A. C: 41A. There was no FOP (fall in potential) on the line-side of the 3-pole starter when the motor went across-the-line; and there was no voltage drop across any of the contacts to the load side. I calculated the voltage imbalance as approximately 2.2%. I'm thinking either a step-down transformer within the building, or possibly the utility voltage is off. But I don't want to lose this expensive-oh-so compressor. I'm installing a phase monitor and a new CB. Any help and pointers would be greatly appreciated, and thank you in advance.