three phase 240 volt delta, ungrounded, no neutral. Voltage to ground phase 1 is 120 volt, phase 2 is 120 volt, phase 3 is 240 volt, all voltages between phases is 240 volts: whats up?
It sounds more like a Hi Leg Delta where one of the transformers has a center tap ground. Typically the hi leg would be about 208 to ground.three phase 240 volt delta, ungrounded, no neutral. Voltage to ground phase 1 is 120 volt, phase 2 is 120 volt, phase 3 is 240 volt, all voltages between phases is 240 volts: whats up?
To echo Augies post, what type meter was used and might the 240 to ground reading be closer to 208?
Having 120 volts anywhere in the system indicates a winding is center grounded even if there is no neutral.
Roger
It can not be an ungrounded system with the voltages you posted if the meter is correct.it is an electronic meter the voltage to ground on one leg is 240/250 volt it is a true floating sys which pasadena no longer lets installiation thanks for the reply
Are there true ungrounded deltas..?
I was directed several years ago by an engineer to install a system in an existing building for several machine tools.
Why I ask is several years before that it was mentioned to me that you always want to ground one leg because if you don't, a leg may ground in the field and you would never know and you would be creating potential to ground.
Thank you
I agree. Decades ago I worked at a steel mill with a 480V ungrounded delta system. On day one of orientation I was told to cease using phase-to-ground measurements for anything because they are meaningless on an ungrounded delta system. “Officially” the voltage reference to ground from any phase is zero, but in practice the readings can be anywhere from 0 to the full line voltage depending on total circuit leakage capacitance. In this case there could simply be machines using single phase 240V connected to those legs that have components in them with enough capacitance to ground that it reads 120V out of pure coincidence.If it's truly an ungrounded 3 phase delta system, voltages to ground are somewhat meaningless.. Might be "capacitance" type voltages which will change depending on various items including the type meter being used to make the measurement.
To echo Augies post, what type meter was used and might the 240 to ground reading be closer to 208?
Having 120 volts anywhere in the system indicates a winding is center grounded even if there is no neutral.
Roger
I read this to say that since he sees no neutral that the assumption is made that it is ungrounded. He did not provide any solid proof that it was ungrounded. While his voltage measurements to earth clearly imply a secondary winding with a center tap that is earthed.three phase 240 volt delta, ungrounded, no neutral.
Yes he does but barring a meter error the numbers say it is grounded.The OP says it is ungrounded.
Are there true ungrounded deltas..?
I was directed several years ago by an engineer to install a system in an existing building for several machine tools.
Why I ask is several years before that it was mentioned to me that you always want to ground one leg because if you don't, a leg may ground in the field and you would never know and you would be creating potential to ground.
Thank you
I agree. It may not have been intentionally grounded by original installer, but at some point there had become a ground at midpoint of one side. Someone may have improperly tried to connect some 120 volt loads and created this condition.Yes he does but barring a meter error the numbers say it is grounded.
Roger